- New Jersey
- Journeyman Electrician (retired)
Receptacles are no longer permitted within the 3' of a tub or shower. Don't know what people with the $2000 toilets that require power are going to do. :slaphead:
Is this in the 2020 NEC?
Might be impossible with some small bathrooms
210.52(D) Bathrooms.
At least one receptacle outlet shall be installed in bathrooms within 900 mm (3 ft) of the outside edge of each basin. The receptacle outlet shall be located on a wall or partition that is adjacent to the basin or basin countertop, located on the countertop, or installed on the side or face of the basin cabinet. In no case shall the receptacle be located more than 300 mm (12 in.) below the top of the basin or basin countertop. Receptacle outlet assemblies listed for use in countertops shall be permitted to be installed in the countertop.
Al, one issue with your install
Dennis, re-read Rob's OP. He's asking about toilets that require a cord and plug connection.
Yes, I stop at 3' from the tub...Missed the toilet part. I was wondering why you had that in your post..hahaha
...3' from the tub
406.9(C) Bathtub and Shower Space.
Receptacles shall not be installed within a zone measured 900 mm (3 ft) horizontally and 2.5 m (8 ft) vertically from the top of the bathtub rim or shower stall threshold. The identified zone is all-encompassing and shall include the space directly over the tub or shower stall.
Exception: In bathrooms with less than the required zone the receptacle(s) shall be permitted to be installed opposite the bathtub rim or shower stall threshold on the farthest wall within the room.
If there's a modern style curb less shower you're out of luck.
I'm too lazy to look up the substantiation for this one but I would bet there isn't any real world issue other than someone thinks this is a good idea. Unless people are dying from the receptacle being near the shower this is another example of stupid code overreach. If someone on this forum wrote this PI don't be offended by my opinion but this one falls into if ain't broke don't fix it category. :slaphead:
Not I so I am not offended. If I did write a proposal that was accepted and someone didn't like that would be okay also. Seems like they didn't like my proposals this year.... I tried to get the length of wire increased in the case of a service change where you would avoid afci. They didn't like it but they did add the part where the wire inside the panel or jb does not count for the 6'-- half successful anyway