Different situation than other thread on parking lot lighting.
From the control box there are 2 circuits, 1 heads east, the other heads west. There are maybe 22-28 street lights on each circuit (just estimating).
Each one is on a 2-pole 50-amp breaker. The panel is single phase 120/240. The lights are daisy chained with direct burial wire, not in conduit.
The 2 circuits are controlled by a photo-cell through a contactor.
The lighting circuit has worked fine for many years.
The lights are HPS, not sure of the wattage. It appears that on each circuit the lights are set up for alternating phases (L1, L2, L1, L2.... ) sharing the neutral.
One circuit (heading east) periodically trips the breaker. It probably happens about every 2 week, so not consistent.
Nothing related to the actual lights has changed other than general maintenance by the city maintenance guy.
I checked everything in the control box and everything seems ok. Voltage is fine, photo-cell is working fine, contactor is pulling in and releasing fine.
Current draw on each leg is around 12 - 19 amps. Also checked current draw on neutral, it was around 11 amps.
Without it being a consistent issue it's hard to troubleshoot. If it was consistent I would play around with splitting the circuit up (L1, L2) and try to narrow down the issue that way. The lighting circuit has work without issue for years until this started happening (within the last couple of months).
One theory that the city maintenance guy has is the the POCO bored in the vicinity about a year ago and maybe they nicked a line.,
I'm not sure what troubleshooting steps to take until it becomes a more consistent problem.