NewSilver
- Silver City, NM
I have a customer with a Federal Pacific panel and they simply don't have the money to hire me to replace the panel. Are there any safe replacement breakers for this situation?
Connecticut electric makes UL listed replacements.
Who is asking for the replacement and why? If the customer is not having any problems leave it alone till the time is right for him or her.
That's at least half the problem right there. Customers never appear to be having problems if they never trip breakers. But how do they know it's not because the breakers are simply not tripping when they're supposed to, and they're unknowingly drawing more amps than their circuits are rated for?
Because the failure rate of FPE breakers is not any greater than any other brand installed of the same age.
I've inspected several FPE & Zinsco panel changes where the EC told me the H/O's insurance told them they won't pay for any problems with FPE or Zinsco.
| FAILURE CONDITION | FAILURES | |
| % (#failed / #tested) | ||
| Before Mechanical Operations | After Mechanical Operations | |
| No-trip: 200% of rating, both poles | 0% (0/122) | 1% (1/107) |
| No-trip: 200% of rating, individual poles | 1% (3/244) | 10% (21/214) |
| No-trip: 135% of rating, both poles* | 25% (31/122) | 36% (39/107) |
| No-trip: 135% of rating, individual poles | 51% (125/244) | 65% (144/220) |
| Trip: 100% of rating, both poles* | 3% (4/122) | 6% (7/111) |
| Dielectric Breakdown (short)* | 0 | 1% (1/111) |
| TABLE 1 - SUMMARY OF FAILURES *UL 489 Test Conditions |
I respectfully disagree with Curt's comment as well as some of the comments that followed. I am in the insurance industry, and the concern with the Stab-loks originated from actual fires, a 2011 Consumer Product Safety Commission (CPSC) notice (83-008), and the independent research at http://www.fpe-info.org/Hazardous FPE 171110.pdf. which was updated in 2017.
The CPSC stated explicitly that they had concern about the Stab-Loks' non-compliance with the UL standard ((1983, re-emphasized in 2011), but could not base their concerns on any data because there weren't' funds available within the CPSC to do the research necessary to check the anecdotal evidence. The CPSC subsequently closed their file despite the fact that FPE had filed fraudulent UL reports and that UL, EXXON, and numerous other principals to the suit advised fraudulent activity.
There have been numerous comments citing tests that show acceptable Stab-Lok performance. I would like to see this data. I do not argue with the fact that the frequency of actual fire/loss is low, but that is true for all circuit breakers in the history of circuit beakers. What is known is that there have been fires related to Stab-Loks, and there have been observed conditions of welded contacts, which were fortunate observations in that the need for tripping had not occurred. .
Forgive my informal tone, but I'm hearing a bit of, "It never happened to me so it will never happen."
FPE Stab-Lok® Calibration Test Report - Failure Rate Summary
CPSC-C-81-1429 December 30, 1982
Final Report: Contract CPSC-C-81-1429
Date: December 30, 1982
Submitted by: Jesse Aronstein (original contains signature)
WRIGHTVM MALTA CORPORATION. Malta test station, Ballston Spa, New York 12020 518-899-2227 1.0 SUMMARY
Calibration tests have been performed on 122 two-pole Federal Pacific Electric circuit breakers. The calibration tests were performed -in accordance with UL Standard 489 except for or a difference in the sequence of calibrations. UL 489 is the applicable standard that the breakers are presumed to meet. In most cases, the calibration tests were repeated after 500 off-on mechanical operations of the toggle handle..
The circuit breakers tested were supplied by CPSC and came from several sources. Most were provided to CPSC by Federal Pacific Electric, some were purchased new by CPSC staff members at retail outlets, and a few were removed from existing installations. The breaker ratings tested were 30 A (30 two-pole breakers tested), 40A (35), 50A(20), 60A(7) and 80A (30). The tests include performance at 100%, 135%, and 200% of ratings, and dielectric tests.
A substantial number of breakers failed the calibrations testing, both before and after the mechanical toggle operations. Failures were evident with both poles carrying current as well as with one-pole operation. Specifically, the failures are summarized as follows:The failures appeared. among breakers of all ratings, none were failure-free. Most of the "no-trip' conditions were sustained for four hours well beyond the UL specification. These were not marginal failures with respect to the failure criteria. The data suggests that, on the average, the mechanical operations result in increased failures. This was .'not strictly the case on a sample-to-sample basis.
FAILURE CONDITION FAILURES % (#failed / #tested) Before Mechanical Operations After Mechanical Operations No-trip: 200% of rating, both poles 0% (0/122) 1% (1/107) No-trip: 200% of rating, individual poles 1% (3/244) 10% (21/214) No-trip: 135% of rating, both poles* 25% (31/122) 36% (39/107) No-trip: 135% of rating, individual poles 51% (125/244) 65% (144/220) Trip: 100% of rating, both poles* 3% (4/122) 6% (7/111) Dielectric Breakdown (short)* 0 1% (1/111) TABLE 1 - SUMMARY OF FAILURES
The failures relate to hazardous conditions in at least two ways. First, a fault in the wiring or utilization equipment which causes excessive- current-can result in fire if the circuit is not opened by the breaker -- this is its principal functional requirement.
Secondly, it was determined in these tests that some of the breakers overheat to hazardous levels when subjected to overcurrent conditions (due to their own failure to trip) for sustained periods of time.
The overheating can result in incapacitation of the breaker (i.e.: it will no longer open under any condition), and the temperature can be high enough to ignite fire in the vicinity of the breaker, as evidenced by charring of the case on some samples.
https://www.cpsc.gov/search?site=cps...ry=Siemens+ite
let’s just change them all out...
all the data is in for the stablocs.
Anyone got failure rate data for the other breakers?
Sure, FPE got caught with their hand in the cookie jar so to speak. Yes, punishment came swift by the company acquiring them.
but... how many other breaker types fail that insurance company and home inspectors fail to recognize?
will the insurance company stop insuring panels with aluminum bus? Bulldog or challenger breakers?
Pushmatics??SquareD?
You don't have anything that compares failures of other breakers of the same vintage. On top of that all you really got is a whole lot of stuff that says not very much about actual fires in houses.
The problem with Stabloks is that they don't meet the UL standard,
According to your post, it is the FPE 2-Pole breakers that don't meet the 1982 UL Standard, particularly at 135% rating. But it appears at 200% the failure rate is much lower.
Were any earlier breakers tested, like those manufactured earlier than 1982?
Do you have data on the performance of 1-Pole breakers, or are they condemned simply by association?