Vince P
- Kansas City
Any insight on this would be most helpful.
We installed 240 Delta with a 208 high leg to 480/277 WYE transformer. The 240 Delta is the line side and the 480 is the load it feeds, or is fed depending how you look at it the PV Inverter. The 240 Delta is connected on the line side of the system between the meter and the MDP of the facility. When we went to test the system the 208 leg immediately blew the fuse. There was no load on the 480 side as the disconnect was off. I double checked to make sure we had connected the 208 high leg to right location on the transformer. This transformer has the neutral on both the delta and the WYE sides. Our construction drawings indicate that we are to land on the neutral on both the Delta and the WYE sides. I contacted the Inverter manufacture and the inverter does need a neutral to work properly. My question after doing some digging is the neutral on the line side causing the problem? I did a conductivity check on the 208 conductor to ground ( I disconnected the conductor and checked to make sure there was no conductivity ie. we skinned the wire in the pull or something). When the high leg conductor was disconnected from the transformer there was no conductivity, however when I reconnected it to the transformer it was showing conductivity to the ground. Since in this case the 240 delta is the line side I am not sure the neutral is even needed.
Thanks for any help
Vince
Thanks for any help
Vince