fcfjr
- Santa Rosa, California
- Electrical Contractor
Is there no legal way to intercept the conductors from the meter, hit the ATS, and return to the panel?
I am in the same situation in AZ and using exact same panel from Eaton. My plan was to turn off main breaker, unbolt main breaker from buss and put in a lug for 2/0 on each of the phase bolts to feed ATS, and then use the Eaton snap on BR pass through kit on the buss to refeed the panel. 4 2/0 wires is a lotto fit in a panel though. I understand that it probably is changing the listing but at least it is after the main breaker what I am confused about is if you turn off the main breaker you still have no way to stop the generator from kicking on in the event of firefighters needing to come but even if they pull the meter the generator will kick on and there will be power in the house that is on fire.
That wouldn't fly here as the feed through kit is not bolted down, then add modifying a listed panel.
Equipment left the factory listed as is. Punching your own holes in the cabinet could just as easily be called modifying the product and void the listing, yes/no?
Where do we draw the line on modifications being permitted per the listing other than if instructions specifically allow a particular modification?
It has gotten to the point anymore you can not fabricate anything or even make the slightest modification without someone telling you you aren't allowed to do that. How do ideas ever become new products if people don't have the ability to tweak things to fit a particular need here or there? Most the time an idea starts out there in the real world where problems are occurring and not in a lab.