Isaiah
- Baton Rouge
- Electrical Inspector
Does the Code require bonding to rebar throughout the plant (e.g. refinery) or only at services?
The NEC doesn't even say that you need to connect to the rebar. It does say that if your rebar qualifies as a concrete encased electrode (CEE) then you have to use a CEE. It can be the qualifying rebar or 20' of #4 bare copper in the footing.
NEC 250.50 requires bonding to rebar where available at Service entrance
Where available was changed to where present, when the CEE was required. Where available was not enforceable for requiring use of the rebar
NEC 250.50 requires all electrode types in 250.52 (A) (1) through (8) at each “building” or “structure served”, to be bonded together to form the grounding electrode system.
250.52(A)(3) Concrete-Encased Electrode. A concrete-encased electrode shall consist of at least 6.0 m (20 ft) of either (1) or (2):
(1) One or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not
less than 13 mm ( 1 ∕ 2 in.) in diameter, installed in one continuous 6.0 m (20 ft) length, or if in multiple pieces
connected together by the usual steel tie wires, exothermic welding, welding, or other effective means to create a
6.0 m (20 ft) or greater length;
or
(2) Bare copper conductor not smaller than 4 AWG Metallic components shall be encased by at least 50 mm
(2 in.) of concrete and shall be located horizontally within that portion of a concrete foundation or footing that is in direct
contact with the earth or within vertical foundations or structural components or members that are in direct contact with
the earth. If multiple concrete-encased electrodes are present at a building or structure, it shall be permissible to bond only
one into the grounding electrode system.
That is correct so if your building had 20' or more of 1/2" of larger rebar in the footing you are required to install a CEE but that does not mean that the CEE has to be the rebar. According to 250.52(C)(3) a CEE can be the aforementioned rebar OR 20' of #4 or larger copper conductor. If you choose to use the copper conductor you are not required to use the rebar. The last sentence of 250.52(A)(3) tells us that if more than one electrode is present you are only required to use one. So if the copper CEE conductors are what is preferred because they make someone feel all warm and fuzzy you can skip the rebar altogether.
that is not what it says. bonding is only required if the rebar qualifies as a GE.
Last house I built ;had a note on rebar drawing to spot weld rebar together.
Structural examiner redlines that, said no welding allowed, as the rebar required overlap and tie wires were sufficient for CEE and structural AHJ guys worried about incompetent welding reducing cross section of rebar.