mshields
- Boston, MA
If you are going a substantial distance with a feeder such that you have to increase phase conductors for voltage drop, you would never have to increase the Equipment Ground accordingly would you?
Yes, and for the same basic reason: impedance, especially under fault conditions.If you are going a substantial distance with a feeder such that you have to increase phase conductors for voltage drop, you would never have to increase the Equipment Ground accordingly would you?
If even states that in 250.122(B) 2014 NEC book . Outstanding.Wire Type EGC need to be increased in size proportionately...2020 NEC 250.122(B)
Yeah, I got burnt on that one in an inspection years ago.If even states that in 250.122(B) 2014 NEC book . Outstanding.
Well...there is a new twist for 2020...ungrounded conductor increases in size for 310.15(B) ambient correction or 310.15(C) more than 3 current carrying conductors are excluded from the rule...
Wasn’t this already (possibly) the case? Or at least debatably so? Perhaps it is just clarified now. The wording has been something like “...increased in size from the minimum size that has sufficient ampacity for the intended installation...”
I’ve heard reasonable arguments that this means that the ungrounded conductor size you start with are AFTER temp corrections and CCCs in a raceway considerations. Because THAT is the minimum size for the intended installation (or at least that’s what the argument is). Any increase after that adjusted size, such as for VD, would mean an increase in EGC is needed.
Yes, that was my thinking also. Correction factors didn’t need upsizing EGC.Wasn’t this already (possibly) the case? Or at least debatably so? Perhaps it is just clarified now. The wording has been something like “...increased in size from the minimum size that has sufficient ampacity for the intended installation...”
Well...there is a new twist for 2020...ungrounded conductor increases in size for 310.15(B) ambient correction or 310.15(C) more than 3 current carrying conductors are excluded from the rule. But, increase for voltage drop on long runs would need EGC up-sizing proportionately...well unless (new exception) some qualified person (smart engineer) can prove otherwise in accordance with 250.4(A)(5) or (B)(4)
Seems like with parallel conductors 250.122(B) is not well defined under either the 2017 or 2020 wording. Example:
190A feeder, one conduit, no temperature correction. You could use (3) 250 kcmil Al conductors for a 75C ampacity of 205A. Or you could use (6) 1/0 Al conductors for a 75C ampacity of 192A after the 0.8 adjustment factor. (2) 1/0 conductors have an area of 211.2 kcmil.
So if you choose to use 250 kcmil Al conductors, have the ungrounded conductors been "increased in size"?
Cheers, Wayne