Lioneye
- Northwest USA
- Master Electrician, State Electrical Inspector
Hi,
I have a customer with an existing 240V, 30A well pump circuit, installed 80' remote from a residence. Installed 30 yrs ago, underground 10/2 UF cable, with"No Equipment Grounding Conductor" (Yup... confirmed at both ends). As such, we have phase to phase OCP, but no phase to ground protection. Can a 2-pole GFCI breaker with no connection the the neutral or ground bar in the service, capture and react to a phase to ground event at the load end? Prob still equal current if the circuit is closed, but it when it opens would it trip? I know the breakers need a neutral connection (st the panel) for the test function to work... Any insight would be appreciated, especially if it has some documentation I can pass along. Panel is a 200 A, Homeline.
Thanks!!
Thanks!!