wmacdaid
New User
- VelcroUSA Manchester, NH
- Electrical Control Tech
Does a 3 phase motor starter protect against single phasing or do I need a 3 phase monitor?
It's been a long time since I installed a motor starter, but I thought the whole purpose for a motor starter was to protect against single-phasing.The simple answer is that some three phase motor starters contain electronic overload protection which also detects single phasing even on a lightly loaded motor.
Others contain thermal overload protection which by its mechanical design trips at a lower current when single phasing is present.
And some contain overload protection which is not sensitive to single phasing and can lead to a burned out motor.
Note that it is relatively easy to detect single phasing when you try to start the motor. It is harder to detect single phasing when the motor is running but lightly loaded, since it will continue to turn at near synchronous speed and without overcurrent on the remaining phase. (Think about a rotary phase converter.)
The one absolute requirement for a motor starter is to provide overload protection which the short circuit and ground fault protection for the circuit can not generally do. If single phasing results in an overload it will then protect the motor.It's been a long time since I installed a motor starter, but I thought the whole purpose for a motor starter was to protect against single-phasing.
... do I need a 3 phase monitor?
Exactly. The motor itself plus the collateral damage.How expensive is it to replace the motor?