Hey Everyone,
Hope you are all doing well. I have been doing power systems studies on SKM power tools for a couple years now and when I do my studies I always try and do my reports starting with the utility provided transformer size / impedance and fault current information at the utility transformer primary bushings. The utility will provide this information after I request it. Usually I consider what the utility provides me as the source for my maximum fault current information, but sometimes I have seen people calculate the maximum fault current based on what could possibly be provided in the future. For instance, I am doing a study in California and the utility provided me with what is actually at the service entrance, a 750 KVA transformer and what is capable of being provided in the future, a 2500 KVA transformer. Obviously the 2500 KVA transformer would provide way more fault current and this would change the ratings for a lot of my equipment. For anyone who does power systems studies, when you calculate your maximum available fault currents do you use what is actually provided or do you look at would could be provided and use that as the basis for maximum available fault current?
Best Regards
Best Regards