Hello, I have a motel that has 18 rooms and will be converted into 14 apartments. It has a 1200 amp 120/240 3/phase service currently but the poco is going to change to to 120/208 system. According to my load calculations I can get by with around 400 amps. Each apartment is approximately 650 sq ft and has a water heater, mini-spit system for heat/air, range, dishwasher, microwave. I'm wanting to install (2) 400amp panels and feed 7 apartments off each panel. The longest distance is around 160 feet. My question is, can the feeders to each apartment be #2 aluminum ser or should they be 1/0 ser? According to my calculation each apartment with the optional method would be around 91amps. I know there is an 83 percent rule which looks like it should apply to feeders also. I'll have 100 amp panels in each apartment. I also have 5 dryers and washers that I'll split between the 2 panels.