mbrooke
Batteries Included
- United States
- Technician
Is there any risk in not using it? Around here there are plenty of installations without it showing no signs of overheating.
What about oxidizing?
Formula: Risk rises as time lapses
Ok, go back to bed
Over time the connections will oxidize. It will take longer that a week, a month or year to see the results. Most of the meter enclosures that I use (usually Milbank) have a dab of some sort of anti-oxident inserted in the lug cavities. That said,, if you've ever seen the commercial for Frank's Hot Sauce - "I put that $#@& on everything"Is there any risk in not using it? Around here there are plenty of installations without it showing no signs of overheating.
The older aluminum alloy was as issue but the new alloy does not require noalox.. Of course, old school here we use it anyway
It's not required so I'm not sure why the termination would deteriorate over time if properly installed in the first place. IMO it's cheap insurance but you are not required to use it.
That is common BS inspector call, 110.3(B). I have not checked every one, but have found statements from several AL conductor mfgs saying noalox is optional not required.Thats what I'm thinking- but I'm being told that manufacturer instructions require it. I'm not finding which instructions call for it though. Not NEMA receptacles, not breakers and not enclosures. I could be wrong on one of those.
Hats off to you!Now thats an educational read
Oxide Inhibitor Oxide inhibitor use is considered good workmanship for all 600-volt terminations, whether wired with copper or aluminum conductors. The oxide inhibitor provides a barrier at the connection point that excludes moisture and other potentially damaging environmental substances. Oxide inhibitor must be compatible with the conductor type. Different manufacturers make compounds that can be used with copper only, aluminum only, or both copper and aluminum. Be sure to choose the compound listed for the application. Compression connectors often come pre-filled with the appropriate oxide inhibitor. When connectors are tested for compliance with UL 486B, the conductor is prohibited to be wire brushed or abraded, and oxide inhibitor may only be used if the connector is pre-filled with the antioxidant. Therefore, mechanical set-screw terminations are tested without wire brushing and oxide inhibitor. According to the UL GuideInfo (UL White Book) for wire connectors (ZMVV), oxide inhibitor for aluminum or copper wire may be used if the connector manufacturer recommends its use on the connector documentation. Oxide inhibitor is of the most value when making connections between uncoated copper and aluminum. This type of connection is subject to galvanic corrosion when in the presence of an electrolyte. Since most lugs today are made of tin-plated aluminum, galvanic corrosion is limited except in the case of severe electrolytic environment or significant damage to the connector plating.
The EC grade wire then available was 99.5% pure aluminum, hard-temper and was more notch sensitive than copper building wire. This is no longer true since AA-8000 aluminum alloy building wire is a fully annealed aluminum alloy conductor that is very strong and flexible.
there’s more above. Got a computer full of that stuff. I can’t seem to get it all posted in one sitting without editing...
There is also this info below. Aluminum wire was 99.5% aluminum. It no long is-- see below. In all it seems the best deal is to use anti oxidants on both copper and aluminum but you must be careful not to use the incorrect compound.
Allow myself to add more personal observation to the mix. Previously I did not believe the Noalox "hype". Then I ran into an application that made me a believer.As Steve said, oxidization can take a while. That’s what gave aluminum a bad name, improper installation.