Ladies; Gentleman
Hopefully you can help me to understand a problem we are dealing with - I was called in to troubleshoot why our generators at a certain building were running and had not timed out. When I arrived I found that we had a breaker trip that feeds one side of two substations, which tie over automatically, building normal after tie over. I will not get into details of cause. The problem is that on one side of these units the fire pump feeders are tied in ahead of the main which kept the generators on line. We asked our management if we could turn off while we dealt with tripped beaker problem and fire watch building explaining the problem with running these unloaded, this was denied.
About five hours in one of the paralleled generators tripped offline with a excitation fault. Now before this, we noticed that these generators showed a load of over 600 amps with no load connected, this load was on generators them self, on our protective relays (paralleling gear) and feeder breakers that were open.
Question -
Is it normal to see this kind of current on unloaded generators?
Is the excitation fault on protective relay saying that we have a problem that will cause damage to generator if we were to test? We called in generator rep who started this generator and said all is good? Being I'm not a generator guy does this seem correct? I would think it would need more investigation?
Was the current we experienced caused by this problem and we can expect same on non faulted generator? Thanks!
Question -