Smash
- Philadelphia suburbs, PA USA
Have a steel cutting plant that is having there cranes zipper rail replaced. Found several code problems that will be addressed. Crane operates on 3phase 480V The main Incoming service is 800Amp 3phase 240V. Several transformers scattered around building supply the 480V. Crane now operates on a aging 3 wire system and will be upgraded with a 4th ground wire. Art 610-61 entitled Grounding. The trolley frame shall not be considered as electrically grounded through the bridge or trolley wheels and it’s respective tracks. That’s how it is now
No problem completely understand the need for the 4th ground wire. However the last line in the article “A separate bonding conductor shall be provided” So can that be a simple jumper from the structured steel or do I need to carry the grounded XO terminal from the 480V transformer to the 4th crane ground wire. The 480 V transformer is currently bonded to the structured steel I beam. Surface lug on outside of transformer to lug on I beam. #2 jumper
I’m not sure if there trying to ground the crane or bond the track to the crane or both. The crane is operated from the ground by hanging handheld controls. It’s rides the length of the building.