JoelWEdwards
New User
- City of Lakeland Water utilities
- electronic technician
I am an electronic technician for the City of Lakeland Water Utilities.
We are interested in finding out how to obtain an exemption in the NEC 501.15 (4) Class 1 Division 1 Boundary. Our situation is this. We have 185 sewer wet wells in the city. They have a rigid aluminum conduit that is open in the wet well with a pump lead coming out of it going to a submersible pump that is submerged in sewage. We have a junction box that is between the motor control cabinet and the pump. When the pump has to be pulled for maintenance and rebuilt the conduit seal off has to be busted out and that puts pieces of concrete in the conduit and then the pump wire won’t come out because it is trapped or snagged in the conduit from the concrete. We want to put a C body condulet in the conduit just before the EY seal off so that we can open it, block it off with rags and keep any concrete from going down into the underground part of the conduit run. Our city inspector says we can not do this because of what is stated in 501.15. Having to bust up a concrete pad and rip conduit apart underground because of this we find to be unacceptable. What are your thoughts?