Service LB Access Panels
We have a 4 unit townhouse building. All 4 services run through the attic space. All 4 come down an exterior wall in one unit. The electrical contractor then used LBs to go into the back of the meter.
At a minimum, access panels would be needed at all 4 LBs. But..........
Do the access doors need to be lockable? Otherwise, 1 unit has "access" to all 4 service wires technically.
Do they need to be insulated for an exterior wall?
Is a simple plastic access panel okay?
I am not finding any codes to support any of these ideas.
Is there a good reason why they didn't run the mast on the outside of the building?
I was assuming these were load side of meters, and hopefully there is also a disconnect associated with each meter otherwise most places won't allow that much service conductor "inside"the building.
NEC does not give any clear distance limitation on what is allowed inside, many jurisdictions have limits of 3, 5 maybe up to 10 feet in some cases.
Once you go beyond the service disconnecting means, you have feeders and there is no such limitations.
POCO would likely care less of who might have access past the meters regardless of location of service disconnect.
The OP is not clear if these are service conductors or feeders. As noted that will make a big difference.
If these were feeders and it was legally a condo it would be OK from an NEC standpoint with an access panel. I can't imagine anyone one being OK with an access in their unit though. If this is legally a townhouse you can't have owners stuff going though another unit.
Incredibly poor planning. I'd fire the EC just for being so stupid.