Tulsa Electrician
- Tulsa
- Electrician
New so take it easy on me.
I have a two gang meter enclosure provide by utility
The Neutral is bonded to the enclosure factory( bare bare bolted to can)
Over head drop from utility
Residential two family dwelling
Meter can (enclosure) mounted on concrete siding wood structure
One #4 ran on surface of structure from meter can to single ground rod
#4 GEC landed under lug in side can on Neutral bar
No other GEC conductor elsewhere or second rod
*Yes a second rod should be driven at least six feet away from first and new unlicensed GEC ran from meter to driven rods.
Utility and city require GEC to rod at meter
Plastic service water line and pex water line used through out, no 18" of copper at gas water tank
Gas line Bond not installed however required ( bond only per city)
Now it get good!
For the service entrance conductors they used 2-2-2-4 AL, Yes an SER cable
Ran 20' to the first mean of disconnect which is a 24 circuit 100 amp main breaker load center Located in interior hall way of each dwelling
The termination of this 4- wire cable is whats in question
Line phase connection, OK (black and red)
White grounded conductor(neutral) landed on meter can Neutral lug and on neutral lug in load center.
No for that fourth wire of the SER cable
It is landed inside the meter can on a separate lug bolted to the can via drilled 1/4 x 20 hole, bolt and nut to the enclosure Lug is a 90 c rate CU AL lug
By the way no contact paste( anti oxide inhibitor) use on any AL wire
Now it gets really good!
At the load center location this #4 bare Al which is part of the SER cable is landed on the neutral bar via a split connection under two of neutral bar screws
The MBJ ( Main Bonding Jumper) is also installed (green screw through neutral bus bar into enclosure inside this load center which contains an 100 amp main breaker or first means of service disconnect.
So when I came uncorked it was like talking to the sheet rock wall. I was told it passed inspection and to leave it alone.
By the way did I mention the two 1-1/4 inch hole in the bottom of the meter can to which was no effectively closed. Yea just two hole some one could stick there little fingers in.
I should also mention the the cable exiting the meter can through the siding into structure was ran through a 1-1/4 PVC male adapter with lock nut and bushing
I should also mention the #4 bare copper running to the ground rod was loose under the approve ground rod clamp I mean fall out loose
This installation was done in the city of Tulsa OK
Does it end there? Nope!
This two family dwelling (duplex) was rewired with new NM cable though out.
All the grounded conductors were terminated on the neutral bar
Wonder how they planned on hooking up all the AFCI/GFCI breakers required by the city
In one side it had 10-3 g to the dryer recpt. and on the other 10-2 g again I said what and was told do not touch it and to put in a three wire recpt.
This washer dryer combo set right next to the elect ignition gas water tank.
I found several other issues however you see the first and big one the service.
Now it get good!