Hi,
In our specs, it is mentioned that "support boxes and conduit above ceiling independently."In my opinion, this item is for prohibiting to mount raceways on suspended ceiling.
We have installed our raceways with trapeze type supports as shown below. However, our manager wants to add one supporting rod from every pull boxes to the concrete ceiling.
Most of our boxes are 10x10x5cm dimensions pull boxes. They are like 2-gang device boxes. I found an item below in NEC 314.23.
Can this item be used for powering my arguments or shall we install a rod for every boxes?
314.23
(E) Raceway Supported Enclosure, Without Devices, Luminaires, or Lampholders. An enclosure that does not contain a device(s) other than splicing devices or support a luminaire(s), lampholder, or other equipment and is supported by entering raceways shall not exceed 1650 cm3 (100 in.3) in size. It shall have threaded entries or have hubs identified for the purpose. It shall be supported by two or more conduits threaded wrenchtight into the enclosure or hubs. Each conduit shall be secured within 900 mm (3 ft) of the enclosure, or within 450 mm (18 in.) of the enclosure if all conduit entries are on the same side.

In our specs, it is mentioned that "support boxes and conduit above ceiling independently."In my opinion, this item is for prohibiting to mount raceways on suspended ceiling.
We have installed our raceways with trapeze type supports as shown below. However, our manager wants to add one supporting rod from every pull boxes to the concrete ceiling.
Most of our boxes are 10x10x5cm dimensions pull boxes. They are like 2-gang device boxes. I found an item below in NEC 314.23.
Can this item be used for powering my arguments or shall we install a rod for every boxes?
314.23
(E) Raceway Supported Enclosure, Without Devices, Luminaires, or Lampholders. An enclosure that does not contain a device(s) other than splicing devices or support a luminaire(s), lampholder, or other equipment and is supported by entering raceways shall not exceed 1650 cm3 (100 in.3) in size. It shall have threaded entries or have hubs identified for the purpose. It shall be supported by two or more conduits threaded wrenchtight into the enclosure or hubs. Each conduit shall be secured within 900 mm (3 ft) of the enclosure, or within 450 mm (18 in.) of the enclosure if all conduit entries are on the same side.