Azazael
- North Carolina
- Automation Tech
First time posting but have been lurking in the background for years, so i would like to begin by saying this is a great site for information and member wise.
At my facility we have a 3 phase 600volt service feeding a panel which is protected by a 1000 amp breaker, ground rod supplied at the panel. A 600 amp breaker then supplies 600 volts and EGC to a 600v\480v Y-Y 500kva auto transformer, this is a HPS auto transformer part# Y500PKCH3LOU with the XO kit.
The 480v and ground then feeds another breaker panel for equipment, no connection at the auto transformer XO. When I take DMM measurements with everything off and isolated after the transformer i get odd readings. On the 600v tap i get H1=156, H2=480, and H3=481. On the 480 tap i get X1=86, X2=415, X3=416. Those readings are all line to ground, phase to phase readings are all correct, and phase to floating XO are all correct as well.
The equipment being feed doesn't require a nuetral so the persons installing this set-up did not land anything to the XO lug. I'm fairly certain the XO and EGC ground should be bonded together at the transformer but when i tried this it tripped the 1000amp breaker GFP. The 1000 amp main is a MCB a PowerPact PG1000 with a Micrologic 6.0. I was told to lift the EGC going out to the 480 panel and land it on the XO lug Could some of you more experienced gentlemen please advise on the XO connection?
Thanks for any help on this.