Customer asked for a quote showing a 1-3000a fused disconnect with tap gutter to be located and feed near POCO transformer. The service will feed 4 buildings tapped from gutter to each building. The drawings show no wire or conduit schedule. The first thing that comes to mind is that the disconnect isnt going to have GFPE for disconnect and some of the buildings are 200' to 300' away from 3000a service. I believe they will need to add a 3000a switch board and each feeder for each building will need to have a its own breaker going to each building. I am not sure how to approach the problem because they want to bring service to one location then branch off to each building. The problem is that each build sits a distance away. I am just trying to figure out a better solution because if dont believe as is will work.They show the service equipment to be located near the transfomer out by the road LOL. I am sure there will be a revised drawing needed because based on drawings load analysis/one line the POCO wont even meet with them to discuss the new service.