carloslt
Member
- Location
- Puerto Rico Coast Guard
- Occupation
- Electrician
Hello,
I have been an electrician for about 5 years and two days ago, I found an interesting circuit breakers configuration and I want to know if is acceptable. I found "two breakers in parallel". Two, 165 amp breakers protecting two, 2/0 conductors in parallel going to the same terminal block to feed a chiller. two conductors in parallel is not new for me, but the two breakers are. I am asking because I was not aware of this condition, the equipment was no longer used, and the breakers were "off". When I was tracing the the wires to use that branch for something else, I turned "on" one breaker, finding that the second breaker ("off") was fed back thru the terminal block. It seems to me like an "unsafe condition". This equipment has been disconnected for more than a decade. Thanks.
I have been an electrician for about 5 years and two days ago, I found an interesting circuit breakers configuration and I want to know if is acceptable. I found "two breakers in parallel". Two, 165 amp breakers protecting two, 2/0 conductors in parallel going to the same terminal block to feed a chiller. two conductors in parallel is not new for me, but the two breakers are. I am asking because I was not aware of this condition, the equipment was no longer used, and the breakers were "off". When I was tracing the the wires to use that branch for something else, I turned "on" one breaker, finding that the second breaker ("off") was fed back thru the terminal block. It seems to me like an "unsafe condition". This equipment has been disconnected for more than a decade. Thanks.