(2) Cord-and-plug-connected or permanently connected utilization equipment other than luminaires.
I assume this meant indoor lights cannot be powered from 480V single phase circuits?
210.6(D) 600 Volts Between Conductors. Circuits exceeding
277 volts, nominal, to ground and not exceeding 600 volts,
nominal, between conductors shall be permitted to supply the
following:
I agree, It appears to state that luminaires cannot exceed 600v so 480v would be allowed.
Is this from a 480Y/277 volt system? Would a 480 circuit exceed 277 volts to ground?
Yes, 480Y/277V system, never use 480V-single phase lights for indoor lighting, but curious about the rule...