Bluebird
- South Carolina
- Electrical contractor
I need help on an issue I'm having at this time and nothing I've encountered before. This is a tiny home. I have an arc fault breaker that is tripping on the living room circuit. I haven't gotten down to run any specific testing yet, but wanted to see if anyone has had this similar situation before I spend time testing this out. I have managed to identify that when the occupant has a few items on such as the light, ceiling fan, lamp, and another LED light, and they either take a shower, run dishwasher, or washer the circuit trips. This is not every time. With this it makes me think it is when the gas tankless water heater is running. Doesn't do it every time someone uses hot water.None of these two are tied together and they are not interconnected in the electrical panel such as the neutrals mixed with the arc faults. Now let me confuse the situation a little by saying this has been happening in 4 of the tiny homes on site. This would be 4 out of 25 homes. The first one, I switched two of the breakers and it hasn't tripped at all again. On the second one, I switched the breakers as before and still having a tripping issue with the same circuit but on the different breaker. I haven't done anything yet with the other two. All the terminations in the panels are tight and all are new panels, breakers. Why would something be causing an arc fault to trip on another circuit that is not an arc fault and none of the wiring are connected except in the electrical panel?