I agree and this controller is in a weatherproof building so no rain,water, dust etc, will not enter the cabinet.If by that you mean NEMA environmental specifications, as in NEMA 1, 3R, 4, 12 etc., the NEMA 2 is basically NEMA 1 + it is "Drip Tight", meaning FALLING (but not wind driven, hose directed, sprayed etc.) drops of water will not enter and build up inside of electrical equipment.
As a general rule, CONDUIT does not have a NEMA rating, but how it enters and exits enclosures would. If you glue PVC pipe and use proper fittings, yes, it would exceed NEMA 2 environmental specs.
Entries in bottom or in sides below live components don't effect watertightness for falling water, can be an issue with pressurized spray or wind driven rain or similar though.I did not use a Meyers hub because the only place to enter this cabinet is from underneath.
Therefore I saw no need to use one. I guess if I use a sealing washer or lock nut then it should comply.