- New Jersey
- Journeyman Electrician (retired)
You're voltage is about 3% low, and the transformer has 2.5% steps. So like Larry said move one step, in your case one tap closer to each fixed terminal (H1, H2, or H3) on each winding of the delta. So move to the tap with the next higher number, which is labeled with a smaller primary voltage.
This gets you a 2.5% higher volts-per-turn on the primary, and therefore also a 2.5% higher volts-per-turn on the secondary. One step would give you 207V. Two steps would give you 212V.
I hadn't done the math. I would definitely opt for 212v with no load, if not higher.One step would give you 207V. Two steps would give you 212V.
You aren't going to get there. If the equipment really NEEDS 240 (or 230), you'll either need a different transformer, or another step down unit or boost unit(s). Which is best depends on loads and costs.The issue is that there is equipment designed to run on 1Ø, 240 volts. Since our output is only 202 volts with no load they're blaming us for their equipment not working. I just want to change the taps to get it up to where they can no longer blame us if their stuff doesn't work.
Transformer taps can be confusing.
... half the times I get it the opposite way I intended!
Think of it as that you're adjusting the voltage-to-turns ratio, not the voltage itself.I agree. I always have to think about for several minutes, and still half the times I get it the opposite way I intended!