Possibility of 120/208 3 phase open delta?

Status
Not open for further replies.

BTC

Member
Location
Sacramento
Occupation
Electrical Engineer
Hi there. I am an electrical engineer who has seem 120/240V, 3 phase, 4 wire open delta (high leg) systems in the past. Question: is 120/208V 3 phase open delta a possibility as well? don't think so, but looking for feedback. Thanks in advance.
 
No, however the high leg to grounded conductor will measure 208.

Roger
 
No, it is not a possibility. the relationship between 208V L-L and 120V L-N does not occur in a delta configuration.

However, it is possible to have an 'open wye' 120/208V connection, although this would not be a common name for it. Two legs (208V L-L) and one neutral (120V L-N) are not uncommon (e.g. in apartment complexes).
 
Last edited:
Hi there. I am an electrical engineer who has seem 120/240V, 3 phase, 4 wire open delta (high leg) systems in the past. Question: is 120/208V 3 phase open delta a possibility as well? don't think so, but looking for feedback. Thanks in advance.
Just an additional minor note, you can have a 120/240 high leg system with either an open or closed delta. In some parts of the country it is very uncommon to see the closed variety. In others, it's the opposite.
 
Just an additional minor note, you can have a 120/240 high leg system with either an open or closed delta. In some parts of the country it is very uncommon to see the closed variety. In others, it's the opposite.
I have a northern MO client with a 120/240 high-leg closed delta, and another client in southern IA with an open delta...only two primary phases on the pole at this site, the third phase got left behind a couple miles upstream.
 
I have a northern MO client with a 120/240 high-leg closed delta, and another client in southern IA with an open delta...only two primary phases on the pole at this site, the third phase got left behind a couple miles upstream.

An open delta still require all three phase conductors, it is simply missing one set of transformer windings and core.
An open wye requires two phase conductors plus a neutral.
You may have a 'ground return' neutral. I have never heard of a ground return phase conductor.
 
An open delta still require all three phase conductors, it is simply missing one set of transformer windings and core.
An open wye requires two phase conductors plus a neutral.
You may have a 'ground return' neutral. I have never heard of a ground return phase conductor.
That is how Seattle City Light does their open delta banks, even when all three phases are right there. Here is the construction plans:

 
How about a two pot 120/208 three phase from two primary phases?
 
A delta connected primary requires all three phases, even if it is 'open' (only using two sets of transformer windings).
If it uses a neutral point, then it is an open wye primary.
Yes, I know...
i would go so far as to guess 90 percent of what people call an open delta is really an open wye, open delta bank.
if it is two phases on the primary it is...

my iPad keeps asking me to accept cookies to post, Im having a hard time posting...

maybe time to restart.
 