I have a circuit with continuous current @ 216.9 A. 216.9 A x 1.25 = 271.125 A so fusing at 300 A. 90° C conductors, three phase 4 wire circuit so using 80% adjustment per Table 310.15(B)(3)(a). Looking at 300 MCM @ 320 A under 90° C rating. 320 x 0.8 = 256 A. So technically ok to use 300 A fuses per next size up rule 240.4(B).
The question is can one use the next size up rule for the 75° C terminals that are rated 285 A with 300 MCM? 285 A is still greater than 125% of the continuous current (217.125 A). 240.4(B) speaks more to conductors and doesn't mention terminals... wondering what others are doing.