Stevenfyeager
- United States, Indiana
- electrical contractor
Can you recommend a lightning protector for a house that apparently gets strikes close by fairly often. Thank you
Definitely, I had a customer that lived below a rock quarry, constantly losing his phones and tv’s. Went out to look at it, service came in at one end of the house, phone and tv came in at the other end. Added another ground rod at the phone/tv end, buried a #4 bare copper in the yard and connected both points. He never had a problem again!Also, if you are concerned about nearby lightning strikes, be very careful about _bonding_, making sure that all incoming services (electric, phone, cable) are connected to the _same_ earth electrode system.
-Jon
So if the POCO has one, that should be good enough ? I've seen POCO install those.A type 1 SPD is installed on the supply side of the service, IE ahead of your main disconnect. This would be a type the POCO would install. Check with your POCO and see if they have an SPD that goes in the meter socket.
If not, you would install a type 2 SPD at the panel. Install it directly opposite the branch circuit breaker, with no loops or slack in the SPD wires.
And then install point of use SPDs at electronic equipment (type 3). The service SPD reduces the surge, and then the impedance of the building wiring reduces it further, and then your type 3s can reduce if further.
For a Type 2 SPD, I would expect to pay $200-$300. Type 3, I use a Leviton that is about $15.00.
Leviton, Panamax, many good types, just look at the specs and compare
And remember what Mike Holt said
"More is better, you get what you pay for."
Your reference in the 2020 NEC is new (well relocated) Article 242.
So, I should recommend type 1 and type 2 to my customer ? Or all three ?The POCO models that go in the meter socket are very effective as they have zero lead length, the type you wire in have a max lead lenght of 18". Doubling the lead length doubles the impedance.
So IMO the POCO version should be effective but, again, more is better
Thank you !type 1 is the best if available and its a simple install by POCO type 2 has to be wired in at panel
Type 3 is the typicall plug in available at at big box
What you want is
Type 1 and Type 3
or
Type 2 and Type 3
Put the type 3s where there are electronics, kitchen, TV, computer, phones. Like I said I get the type 3 levitons for about $15 and they have really good specs. I thinks its a 5300P
Here is the app manual https://www.scribd.com/document/996...rge-Protection-and-Line-Conditioning-Products
Here is the product catalog
The ZeroSurge, Brick Wall & SurgeX (all use the same technology) point-of-use surge protectors, are well thought of in the pro-audio and high-end hi-fi fields. But they are all extremely pricey.May I also suggest Zero Surge brand point-of-use surge protectors. No MOVs to wear out; 10 year warranty.
ZeroSurge | Protect Your Sensitive Electronics Against Surges
Zero Surge’s series mode power quality filters protect your electronics from damaging surges. Reliable, non-degrading surge protectors made in the USA.zerosurge.com
I've seen nasty pictures of MOV power strips that have burned up. And the "working" light on those strips is usually just a pilot light!The ZeroSurge, Brick Wall & SurgeX (all use the same technology) point-of-use surge protectors, are well thought of in the pro-audio and high-end hi-fi fields. But they are all extremely pricey.
pretty sure you can install a type one anywhere you can install a type 2 or 3.A type 1 SPD is installed on the supply side of the service, IE ahead of your main disconnect. This would be a type the POCO would install. Check with your POCO and see if they have an SPD that goes in the meter socket.