We need a new word. Gronding. Or Bounding.
I have enough trouble with spell check for contactor and contractor, and you want to add another to?
I'm not saying he doesn't talk about grounding vs bonding. He still does that, but he doesn't talk about trying to change the code to equipment bonding conductor he says equipment grounding conductor.
In Europe they call it protective earth which is even more of a misnomer. That doesn't bother me either. I rather like the term. I'm sticking with egc because it's established here in the USA
Maybe Equipment Grounded Bonding Conductor or EGBCWe need a new word. Gronding. Or Bounding.
But that's not a TLA! ):Maybe Equipment Grounded Bonding Conductor or EGBC![]()
What does the EGC do with an ungrounded system (where allowed)?Faults are cleared with grounding conductors, connected to ground terminals. Not bonding conductors and bond terminals.
Yeah, the terminology is confusing given that the function of both overlap in so many areas. I'd prefer choosing just one term and running with it.
Actually he had a 2020 PI to do exactly that. The following was the substantiation for his PI.I'm not saying he doesn't talk about grounding vs bonding. He still does that, but he doesn't talk about trying to change the code to equipment bonding conductor he says equipment grounding conductor.
Many members of Code panel 5 know the history on how the use of the terms ground, grounded, grounding, bond, bonding, and bonded were revised, starting in 2008 Code cycle, to have the terms mean what was intended. The one 'leftover' item was the equipment grounding conductor.
The effective ground-fault current path is comprised of the main bonding jumper, equipment bonding jumper, system bonding jumper, supply side bonding jumper, and the equipment grounding conductor. All of the items that construct the EGFCP containg the word bonding, except one...
By renaming the EGC to the EBC, the Code terms used will be consistent and remove confusion, it just makes the Code intent clearer.
Interesting. I watched the live stream of his new DVD recordings and I know he said equipment grounding conductor.Actually he had a 2020 PI to do exactly that. The following was the substantiation for his PI.
That was to include 'heavy fixture'.We went from 'light fixture' to 'luminaire'.....
We still want conductive surfaces bonded together and tied to structural ground to mitigate shock hazards.What does the EGC do with an ungrounded system (where allowed)?
First fault essentially turns it into a grounded system. A second fault will result in fault current which may or may not be enough to operate an OCPC depending on situation.
Some people forget that even if there are no earthed surfaces in the vicinity to complete a circuit measurable (and perceptible) current will flow into (onto?) us based on capacitance to earth.We still want conductive surfaces bonded together and tied to structural ground to mitigate shock hazards.
That is what it is for, I was trying to hint at the fact it is not there for fault clearing on an ungrounded system, and would need to be more than one fault before it will actually even try to do so.We still want conductive surfaces bonded together and tied to structural ground to mitigate shock hazards.
I don't think it would clear anything up because the terminology is about one eight of the problem. Like I said you can call it anything, protective earth, equipment bonding, whatever as long as you know what you are doing or care enough to learn it doesn't matter.....If the name were changed, which I mostly doubt it ever would because it's been around for so long, it would clarify things on what is grounding and what is bonding. Perhaps threads like this would no longer need to come up since it's more clear based on the name.
It wouldn't clear anything up? I obviously disagree and this was part of Mike's PI:I don't think it would clear anything up…
The existence of other problems doesn't mean this isn't a problem that can be fixed.…because the terminology is about one eight of the problem.
We agree more than we disagree. I just choose to build on the vocabulary we already have instead of changing. Instead of trying to get everyone to start talking about bonding why don't we get rid of the term grounding by calling it earthing?The G in EGC has nothing to do with ground/earth for function. Grounding is a specific thing, and this isn't it. So the code change request is really about getting the word "grounding" out of there because it doesn't fit and leads to confusion with actual grounding as defined in the NEC.
"By renaming the EGC to the EBC, the Code terms used will be consistent and remove confusion, it just makes the Code intent clearer. "
And to your other points Dave, changing it to EBC would of course not fix the idiocy by others in the examples you stated. People will continue to be ignorant and misinformed, but this might help. For example, people driving a ground rod at a piece of remote equipment instead of using an EGC because they think "grounding" is an alternative to connecting to EGC since they both have the words "grounding". Maybe that type of thing wouldn't happen as much if people understood what a EGC (EBC?) actually did, and this could be more likely to occur if it didn't contain the word "grounding".
More important to me is that we get the terms nailed down and use them consistently. I was around when this whole idea of adding bonding to the electrical lexicon came of age and as far as I'm concerned it made things worse because it got sprinkled around in the code here and there. I am aware that I have a minority opinion about this and eventually the language will get changed to equipment bonding conductor. I hope it happens soon so I can get the chance to see if I was right before I die. The thing is I don't see the Dirt Worshipers losing any ground yet and that is more of a problem than what we name the green wire.
What matters to me most is that we get electricians who not only understand grounding and bonding but understand theory and conductor sizing and circuitry and all other parts of the job so we can elevate the trade, be more professional, get paid more, and be much more safe.
That's a good point. And there are sometimes options for where that connection is made probably adds to this as well.The fact that these conductors usually all tie together at some point leads to some misunderstanding IMO.
And as I said earlier NEC defines all these terms yet people tend to not pay close enough attention and the fact the base word "ground" is embedded within many those terms they tend to think they all have about same meaning, but they don't. Then on top of that they all tie together at some point (in most cases) and that further reinforces the misunderstanding that they all have about same function.![]()
I certainly don't think the word "bonding" is the answer to everything. It just happens to be one that is already used for the same purpose.. MBJ... SBJ.. SSBJ.. etc.. so it's easy for me to get onboard that train.