Cobe
- Madison IN
- Maint.
I have baxter oven, 208/60/3 146.4 amps 51.3 kw, I need to know what size Shunt breaker to install. I was trying to calculate amp on each leg, to get the correct breaker size.
The label tells you 146.4 amps. Times 1.25 = 183.
IDK the values you can get for shunt trip beakers, but I’m guessing a 200 is close.
146 amps is on the oven, i wanted to make sure what each phase pulled or does it pull 146 amps per phase?Why not use the nameplate amperage of 146 amps which is close to the calculated amps of the oven? {51300/208/1.73=143 amps}
Welcome to the Forum.![]()
Tom, just curious why the 125%? Couldn't he just use 150 amp circuit?
Yes. To both146 amps is on the oven, i wanted to make sure what each phase pulled or does it pull 146 amps per phase?
I hope someday the electrical industry will be able to once and for all exterminate the notion of "amps per phase." It means nothing.
Yup, we take per phase amperage readings quite often for various reasons.While I agree in principal. Ii think electricians will continue to use this partly due to the practice of calculating amps/phase for load balancing as shown on consulting engineer's panel schedules.
Through the past nearly two decades of my participation in this forum, I have seen dozens of posts that, for example, talk about a three phase system that has a current of 300 amps, and ask whether that means 100 amps "per phase." I have also seen the opposite version, the one that mentions a phase current of 100 amps and asks whether that means the "total amps" is 300. That is the nonsense that I would like to see obliterated. So whenever I see the use of either phrase ("amps per phase" or "total amps"), I cringe, and seek to clarify the situation.
If the panel is 208Y/120 and all of the loads are 120 volts isn't the total amperage at 120 volts 300 amps?
In the spirit of this thread, I have to point out that eggs also come in 6 egg and 18 egg cartons, as well as in larger "flats".....
Here's why: If I were to buy three cartons of eggs at a price of $2.00 "per" dozen, I would multiply 3 times 2 to get a total price of $6.00.
This is not an easy concept to grasp. I will start by saying that if John has 5 heaters, each 120 volts and 20 amps, installed throughout his house, and if Jane has 5 identical heaters installed in the repair garage she owns, and if there are 5 more identical heaters in a nearby restaurant, then indeed we have a total of 300 amps of single phase, 120 volt load. If we instead have a 120/208V panel that has 5 of these types of heaters on each of its three phases, we can (IF WE ARE CAREFUL) say again that we have a total of 300 amps of single phase, 120 volt load. Why do I say “careful”? Because that is not, Not, NOT the same thing as saying the panel has a “total” of 300 amps of current.If the panel is 208Y/120 and all of the loads are 120 volts isn't the total amperage at 120 volts 300 amps?
The conductor needs to be 125% anyway and you would have to use a circuit breaker rated for 100%, which at 150A is hard to find and it would have to be stand-alone, not in a panel. Using the 125% loading accounts for the circuit being 80% of the breaker rating and rated to protect the conductors anyway.Tom, just curious why the 125%? Couldn't he just use 150 amp circuit?