david.mullins
- Santa Barbara, CA, USA
- Electrical Engineer
Hello,
We have a large machine that's used at sea. We are developing it in our concrete paved facilities yard. It consists of up to 5 sections, each section is a control panel and a machine. There are servo drives in the panels and servo motors on each machine. It all operates from 3ph 480VAC. Each section requires about 70A continuous with 450A peaks for less than 1 second duration. At sea, it will be powered by generators on the ship with our generator as backup. In our yard, it is powered solely by our generator, a Marathon Magna Plus 280KW, 480VAC high wye, 0.8 pf, 60Hz. We connect it to each panel with 2AWG, 3c + G SOOW cord. (this was all setup before I was assigned to the project.) It is protected by GE Spectra RMS MCCBs with 80A trip rating plugs. We operate it for test once or twice a month
My question is, since this is a temporary installation in a paved concrete yard, is this legit without driving ground rods into the ground or does it qualify under "ungrounded systems" with the grounding conductors in the cable?