hhsting
- Glen bunie, md, us
- Junior plan reviewer
I have plan where fire pump is fed by dedicated utility service. Would fire pump fed by dedicated utility without generator be considered emergency system?
A fire pump, however powered, is an emergency system.I have plan where fire pump is fed by dedicated utility service. Would fire pump fed by dedicated utility without generator be considered emergency system?
Code reference on that, pleaseA fire pump, however powered, is an emergency system.
Perhaps I was a little imprecise. It is a fire and life safety system, and if there was a generator it would be required to be on it. Or you can try to convince the AHJ otherwise. I'll bring popcorn. I would say that the feeder, by dint of serving the fire pump, does not become thereby an emergency system under the definition in 700.2.Code reference on that, please
OP said service.I would say that the feeder, by dint of serving the fire pump, does not become thereby an emergency system under the definition in 700.2.
OP "I have plan where fire pump is fed by dedicated utility service. Would fire pump fed by dedicated utility without generator be considered emergency system?"OP said service.
(A) Special Conditions. Additional services shall be permitted
to supply the following:
(1) Fire pumps
(2) Emergency systems
(3) Legally required standby systems
(4) Optional standby systems
(5) Parallel power production systems
(6) Systems designed for connection to multiple sources of
supply for the purpose of enhanced reliability
You've completely ignored the OP's actual question, haven't you? That's the part in the second sentence.OP "I have plan where fire pump is fed by dedicated utility service. Would fire pump fed by dedicated utility without generator be considered emergency system?"
The emergency system, if present, takes over when the primary power fails. For "emergency system" you can substitute the word "generator". The dedicated utility service would not, as far as I can tell, be considered an "emergency system".I don’t have generator. No generator only dedicated utility service. The service feeder that go into fire pump room, fire pump controller , fire pump itself all that system would that all be emergency system?