I'm drawing a blank guys , would someone be so kind as to direct me to the code passage ? art 230???......~RJ~
NEC 2011 (newest one I could find in the office) 210.25 A + B. Looks fairly clear that in a multi occupancy building common area loads are not to be fed from a tenant meter....... Stop me if I am wrong.
Howard
Thanks guys
I'm into this duplex with nothing mutual & was not sure if i had to do meter #3 or not
~RJ~
One old house I worked on they did something I had never thought of. Used two socket fixtures in common area, and fed one bulb from it's own switch each in unit.I lived in an apartment where each had a switch for basement lights. 3 sets of basement lights to avoid having a house meter.