Greetings all I have a 15kVA 480/240 to 120/240 single phase transformer going indoors at a non-supervised location.
The primary side feeder will have a 40A 480V breaker with #8 THHN.
The secondary will feed a standard residential style 100A main breaker loadcenter.
Everything will be in raceway.
T450.3(B) says I don't need secondary protection on this transformer.
However per 240.4 and the definition of a feeder in art 100 I need to protect the secondary feeder.
The 120/240 loadcenter is a few feet away and has a rating of 100A (main factory installed).
I was thinking of just feeding the 100A breaker with #4 THHN as that matches the secondary nameplate A.
That sails me into the reef of 240.21(C)
Scanning the 6 options under (C):
1 does not apply its dual voltage
2 (1) (b) is not met with #4 @85 Amps
3 is out its not supplying a switchboard or switch gear.
4 Its inside so thats out.
5 is out its not feeder tapped.
6 gets me off the reef but it looks like 240.21(C)(6)(2) will require #3 THHN since they will be protected at 100A.
kinda an academic question at this point but was curious if there was a way to use #4 any of you come up with?
Thanks in advance.
Nameplate:

The primary side feeder will have a 40A 480V breaker with #8 THHN.
The secondary will feed a standard residential style 100A main breaker loadcenter.
Everything will be in raceway.
T450.3(B) says I don't need secondary protection on this transformer.
However per 240.4 and the definition of a feeder in art 100 I need to protect the secondary feeder.
The 120/240 loadcenter is a few feet away and has a rating of 100A (main factory installed).
I was thinking of just feeding the 100A breaker with #4 THHN as that matches the secondary nameplate A.
That sails me into the reef of 240.21(C)
Scanning the 6 options under (C):
1 does not apply its dual voltage
2 (1) (b) is not met with #4 @85 Amps
3 is out its not supplying a switchboard or switch gear.
4 Its inside so thats out.
5 is out its not feeder tapped.
6 gets me off the reef but it looks like 240.21(C)(6)(2) will require #3 THHN since they will be protected at 100A.
kinda an academic question at this point but was curious if there was a way to use #4 any of you come up with?
Thanks in advance.