mikeames
- Gaithersburg MD
- Teacher - Master Electrician - 2023 NEC
Going through questions in Mikes exam prep book there is a question about MWBC. It asks.
Multiwire branch circuits shall______
a. supply only line-neutral loads
b. not be permitted in dwelling units
c. have their conductors originate from different panel boards
d. none of these
Its my opinion the answer is d. "none of these" but the book states that the answer is a " supply only line-neutral loads".
That is clearly stated in 210.4 (C) but then the exception 2 is valid if all ungrounded counductors are open at the same time. Ok I get that, but why is exception 2 even there if 210.4(B) mandates ungrounded conductors be simultanously opened anyway?
So going back to the question, you could have line to line and line to neutral loads. I think the book is incorrect, and I think the code essentially makes 210.4(C) meaningless since 210.4(B) will always invoke the exception. I know 240.15(B) speaks to single pole breakers with approved handle ties as oppose to commontrip but thats not specified in the 210.4(C) exception.
Am I wrong?
d. none of these
Am I wrong?