WiFi Override of Motion Detector
infinity
New Jersey
Journeyman Electrician (retired)
I have a scenario where I want to have a light controlled by a motion detector but I also want to have the capability of turning the light on remotely through a WiFi wall switch. My thought is the run the separate switch leg from the WiFi switch directly to the light on the load (switch leg) side of the motion detector. Everything on the same circuit. Anyone see a problem with this?
Is the motion detector indoors such as on an occupancy sensing switch, or is it outside such as those on security lights?
The reason I ask is that occupancy sensing switches sometimes have extra terminals to allow another switch to be connected for three-way operation.
Sorry yes, outdoor security lights up high (25') on the house, motion sensor lower about 10' above ground.
Use light switch override sequence shown with instruction sheet for most security lights.
That requires you to physically be at the switch, I want something that can be done remotely through a voice command or an app so that's why I want to use a WiFi switch as an override.
Every motion sensor I've seen will go into an always on mode by quickly switching the sensor off/on/off/on and then off/on goes back to auto mode, but I don't know if a phone app to a WiFi switch can do the sequence quick enough.
If I did it your way I'd put a note inside the sensor's bell box with the breaker # and saying, "Switch does not de-energize this control!"
Using the same circuit. Take out your existing switch make motion detector hot all the time. Install a wifi single pole switch with another wire going to the bulb holders than by pass the motion.
When the motion detector comes on it will back feed the wifi switch and like wise with the motion. It should still work.
Why reinvent the wheel? Parallel the switches. The motion sensor lights usually have photocells built in, so they are left hot all the time, with the wifi switch being on the same circuit, the output just ties to the red (output) on the motion sensor. If your worried about the neutral, run 12-3 or 14-3 from the fixture to the wifi switch to power it. I have done this at one of the boss's house. Wifi switch at the attic access hole controlling the motion floods.
No reinvention here, that's exactly how I was planning on doing it. Two switches (one SP, one WiFi) switch #1 controls the motion detector, switch #2 is the WiFi override.
OK.
So, how would you turn the power off if you have to work on it-- or do minor repair.
At 25 feet high that would that would be a pretty hard landing.
Of course you can turn off the power to the whole house.
What if you have to check the power to the light socket i.e. "it is responding to motion or darkness?
Or maybe the light bulb is burned out?
Let’s try some vernacular logic.
SW1 and SW2= 1 (light is on)
SW1 and NOT (SW2) MD (motion detect) =1
So, SW1 and/or SW2 should be both zero (0) no contact in order to disable the power to the light-- in case motion is detected by MD.
MD is not a dry contact unlike a generic relay or contactor that actually breaks the contact. Power to the light via solid state circuitry only transitions from HIGH to LOW.. . . power is still “alive”.
Below is in addition to the Simplified Boolean Logic:
For example, suppose you want to build a security system which only works at night and responds to a door being opened. If you have a light sensor you can treat this as giving off a signal that indicates the truth of the statement:
P = It is daytime.
Clearly Not(P) is true when it is night-time and we have our first practical use for Boolean logic!
What we really want is something that works out the truth of the statement:
R= Burglary in progress
from P and
Q = Window open
A little raw thought soon gives the solution that
R = Not(P) And Q
That is the truth of “Burglary in progress” is given by the following truth table:
P
Q
NOT(P)
NOT(P)AND Q
F
F
T
F
F
T
T
T
T
F
F
F
T
T
F
F
From this, you should be able to see that the alarm only goes off when it is night-time and a window opens.”
Now, the Boolean Truth table is more than you need to answer your question-- that in essence says: “is there anything I need to be concerned of--with regard to this idea?”
The example above is lifted from Wikipedia.
As a side note:
I have designed a circuit that addresses this dilemma --that you are confronting.
But you are only asking:--does “anyone see a problem with this?
At first glance it may look complicated-- actually it is not.(with the right components of course)
You also mentioned that you already have a plan on how to do it. So, more power to you. :)
I can mention more issues that can be stated. . . but that would be for another time.
My install worked for me for more than twenty five years now.
OK.
P = It is daytime.
from P and
Q = Window open
R = Not(P) And Q
P
Q
NOT(P)
NOT(P)AND Q
F
F
T
F
F
T
T
T
T
F
F
F
T
T
F
F
As a side note:
Being an electrician, he would probably turn the breaker off.:)
OK.
As mentioned in Post #10 there are two switches, if you had to work on it you could just turn them both off. If I were testing it I wouldn't bother to turn it off at all.
Will the switch for the motion detector and the wi-fi switch be co-located in the same box and their wires be routed in the same raceway? The reason I ask is that you don't want to parallel the hots or the neutrals from two different locations or you can create a loop where the magnetic fields don't cancel very well. So you want the power to be sourced from one location.
If the switches are from different locations, I'd suggest the following:
From the wif-fi switch run a constant hot, the switch output, and neutral over to the motion detector. Then run a 2-wire switch loop to the motion detector switch (i.e., no power sourced at that switch). That way you could use an existing 2-wire to the motion detector if that's what you have now.
You'd have to turn off the breaker to eliminate power at the motion detector box. But personally, I would not trust a "smart switch" anyway for disconnecting the power for servicing.
This is my plan, everything is new, basically there are 3 locations:
First location will have the two switches (1st floor),
Second location will be the motion detector (mounted under an eave on the house 10' above ground)
Third location will be the actual light a 200 or 300 Watt LED fixture mounted up high on a peak about 25' above the ground.
All of the cables will originate at the 2 gang switch. 14-3 to motion detector, 14-2 to LED light, 14-2 feed to 2 gang switch.
Since the switches will be on the first floor I'm looking for a way to turn the lights on from anywhere in the house (especially if I'm in bed at night) which is what the WiFi override switch is for via a voice command.
Sound like a good plan.
Having the interconnect point of all devices in the 2-gang box will also make it easy if you ever want to change the way it's configured.