CAC-ELEC
- petaluma, ca
- Electrical Engineer
I have a location and they want to install (1) generator on two services. The problem I've run into is that both the services are 240V 3P Delta High Leg. On one service they kept the "B" phase as the high leg throughout. On the second service at the meter equipment they switch the high leg to the C phase and run it through out. Am I allowed to swap the high leg from the C phase to the B phase between the generator disconnect and the ATS for that side? Will this have any issues with GND faults etc? I can't find anywhere in the code this is prohibited but it also doesn't seem to address this specific issue. I am making the generator a separately derived system and putting in 4-pole transfer equipment.