I don't really know where to post this question, so I'm posting it here in the General Electric Forum. If I'm posting in the wrong place, I'm sure the moderator will place this thread in the correct place and correct me.
Here is the question...
Is it possible to get 480 volts at 600 amps form a 120/208 200 amp service by using some sort of transformer?
I have a client that wants to install three, 3 phase, 480 volt, 120 KW Car bottom furnaces in a warehouse suite in a multi suite building and the existing service for the suite is only 120/208 at 200 amps, the building has a 2000 amp service gutter that all of the suites meters tap out of. The client has other equipment and I will also need to utilize 208 for the existing HVAC and low voltage (120 volt) receptacles and lighting. Total connected load for the lighting, HVAC and water heater is 38.7 amps.
We have petitioned the power company for permission to add a 600 amp, 480 volt service to service this one suite, we are awaiting a decision for their engineers. I may need an alternative solution if the request is denied. The only solution I have is it upgrade the 200 amp service at 208 to a 600 amp sevice and increase the voltage with a regular transformer, but the power company may deny that also if it overdrives the 2000 amp main service transformers (on the pole).
I'm just at a loss on alternatives and need some input and I felt this would be a good place to start.
-Talmadge
-Talmadge