We are in the process of installing a circuit for an air compressor and there has been some discussions and debate concerning the installation.
The customer supplied the following package ampacity and we determined the rest:
Package Amps 234.3 x 125% = 292.87 amps
Circuit Breaker in Gear supplying Disconnect = 300 amp thermal magnetic trip standard interrupt
Feeder conductors ran are 350 kcmil THHN Rated 310 Amps @ 75*C
Manufacture requests max 3x550 170M Style fuses. Our 400A heavy duty Square D fusible disconnect of course will not accept these fuses as they are rated 690V.
Our questions are:
1) What would be the recommended breaker in the gear as we haven't terminated the wire yet and could still swap it out if we should go up to a larger size.
2) What would be the best way to handle the fuse requirement or request?
3) Shouldn't the drive protection be done in the compressor and not be our responsibility to be provide in the feed circuit? We have typically always installed a service disconnect outside the compressor based on circuit requirements. There is a drive controlling the motor.
Our questions are: