It's a trailer consist of laundry, recreational room, office rooms, utility room, kitchen.
Classified as "support area for emergency use". It's part of trailer park dedicated for homeless people.
Question is what are minimum requirement for smoke detector?
Should we put smoke detector in each room?
No sprinkler of course. No full coverage FA system.
 
The NEC has an article on mobile homes, your application may not be under the scope of the NEC. I would check with your building official. And smoke detectors are inexpensive (unless a monitored fire alarm system is required)
 
The NEC has an article on mobile homes, your application may not be under the scope of the NEC. I would check with your building official. And smoke detectors are inexpensive (unless a monitored fire alarm system is required)
Are you talking about NFPA 501?
 
No the NEC article, its 550 or so.
I need to look at its scope to see if it applies.this trailer is more like an office trailer.
 
Last edited:
And I will add the NEC covers the branch circuit wiring for smoke detectors, but not the placement or requirements.
 
Art 550 covers mobile homes and mobile home parks, a mobile home is defined as a dwelling unit, so in the OP post question, the NEC does not apply to the trailer in question. What I don't know is what standard would be used for wiring that type of trailer?
 
Art 550 covers mobile homes and mobile home parks, a mobile home is defined as a dwelling unit, so in the OP post question, the NEC does not apply to the trailer in question. What I don't know is what standard would be used for wiring that type of trailer?
It has a kitchen, a bathroom, and a place to park your carcass (rec room). What more does it need to be a dwelling?
 
It has a kitchen, a bathroom, and a place to park your carcass (rec room). What more does it need to be a dwelling?
It's a trailer consist of laundry, recreational room, office rooms, utility room, kitchen.

I don't see where the OP said it had a bathroom.

This is what the code says a dwelling is.
Dwelling Unit. A single unit, providing complete and independent
living facilities for one or more persons, including
permanent provisions for living, sleeping, cooking, and sanitation.

I would treat it like an installation that was not a trailer.
 
We have not answered the OP question if smoke detectors are required, what I commented on is that its not under the scope of the NEC.
 
I don't see where the OP said it had a bathroom.

This is what the code says a dwelling is.


I would treat it like an installation that was not a trailer.
You are correct, I some how assumed there was a bathroom. If there isn't, then clearly not a dwelling unit.

I have access to all the NFPA codes and standards, and none of them seem to deal with office trailers, nor could I find anything in a quick look in the building code. Google also didn't return anything useful.
 