If I feed 120/208 to a piece of equipment that has a 3 phase motor and also take off one leg to neutral for a small circulator., will that trip the GFI?
 
Last edited:
If I feed 120/208 to a piece of equipment that has a 3 phase motor and also take off one leg to neutral for a small circulator., will that trip the GFI?
Depends if the GFCI has a "load neutral" and if it does you must use it for the 120 volt load. If it does not have a "load neutral" you can not supply any line to neutral loads from it, or it will trip.
 
If I feed 120/208 to a piece of equipment that has a 3 phase motor and also take off one leg to neutral for a small circulator., will that trip the GFI?
No, as long as the neutral current passes through the GFCI device, too. The line currents need not match.
 