Bending radius of MV-105 wire - 300.34?

Status
Not open for further replies.

Twophase

Member
Location
USA
Running some MV-105 wire for a 4160V system. Four wires (3/C+GND), all #2 AWG. Per 300.34 (2017), the I understand the bending radius to be 12x the diameter of the wire (including insulation). Looking at the wire I plan to use (#2 AWG, 0.76" diameter), I get a radius of 9.12". I plan to run this through a 90 deg elbow (which has R=10"), down some straight conduit, then through an elbow again, straight for 2 feet, and then a final elbow. One of my colleagues mentioned that there may be a limitation on the number of subsequent bends when using MV wire, but couldn't quote where in the code this is from (if it even is from the code). Any issue with what I have described, provided that the elbow R>wire bending R?

Thanks!
 
Running some MV-105 wire for a 4160V system. Four wires (3/C+GND), all #2 AWG. Per 300.34 (2017), the I understand the bending radius to be 12x the diameter of the wire (including insulation). Looking at the wire I plan to use (#2 AWG, 0.76" diameter), I get a radius of 9.12". I plan to run this through a 90 deg elbow (which has R=10"), down some straight conduit, then through an elbow again, straight for 2 feet, and then a final elbow. One of my colleagues mentioned that there may be a limitation on the number of subsequent bends when using MV wire, but couldn't quote where in the code this is from (if it even is from the code). Any issue with what I have described, provided that the elbow R>wire bending R?

Thanks!

There’s a 360 degree limitation
Look at NEC 358.26.


Sent from my iPhone using Tapatalk
 