JIANDO RC
- Atlanta, GA
- Electrical Contractor
I would like to know if other contractors are having the same levels of frustrations and concerns with CH CH DF breakers. My company currently uses both Square D QO and Cutler Hammer CH series breakers. We have installed thousands of both brands over the last 2 years with very different results. The QO breakers perform just fine with very few call backs and when troubleshooting, there are rarely any signs of excessive heat. Cutler Hammer on the other hand has me very concerned. The breakers are as hot as an incandescent light bulb to the touch. There have been more than a few showing discoloration of the neutrals feeding off of the breaker. Measured with a laser device, the readings show a normal range of 90-100f on standard circuit breakers. The readings on the CAFI or DF breakers range anywhere from 105-148f. The same electricians are installing both brands in the same manner. Their work is top notch so I am skeptical that it is in the workmanship. The fail rate and call backs are especially high when the panels are mounted in the garage of a slab home as opposed to basement installs.
Clamp on neutrals have the highest temps and fail rates over the pigtail design btw.