One other thing. The vast majority of stray voltage problems are caused by muktigrounded systems where you get ground loops, and faults taking multiple paths.
One other thing. The vast majority of stray voltage problems are caused by muktigrounded systems where you get ground loops, and faults taking multiple paths.
Just as an aside in case it might apply, a friend of mine in New Zealand (where Dairies are one of their only stable industries) did a lot of work on the effects of stray voltages that are created by the more extensive use of VFDs now. He boiled his work down to this web page. Worth a look.
Incorrectly installed VFDs cause high frequency stray volages that agitate cows in the milking shed and can severely affect the performance and health of the cows.
I haven’t gotten around to the GF detection yet. The above metallic gutter mounted between two pvc faulted and energized the building frame. Some one noticed it smoking.. PVC was temp fix. Covers inline setscrew Splices we had in our used parts area. Field engineering.