6-2 MC from the panel to the back of an LB.
Unsheathed the MC from the LB and then EMT from the LB directly into a plastic Tesla Wall connector.
A simple run (MC to LB to EMT).
Is this not an acceptable bond? There is an inspector in the area that is failing jobs because he wants a JBox and not an LB as the point of transfer....says the LB is not able to carry a proper bond like the JBox is.
I was under the impression that MC is actually conduit and so is an LB (a conduit body) and EMT is also obviously conduit.
Thanks for any comments and code interpretation.