250.92 (A) Bonding of Equipment for services.
My understanding is,
The CT cabinet, EMT conduit/s compression connectors from a CT cabinet to service main disconnecting means enclosure, cabinet, main disconnect enclosure, cabinet, shall be bonded to the grounded service conductor. Correct?
Service riser RMC connects to the CT cabinet via a compression no thread connector threaded into a myers hub connected to the CT cabinet. (punched 3" KO). The conduit is therefore bonded to the CT cabinet per 250.92 (B) (2). Correct?
250.92 (B)
"Bonding jumpers meeting the requirements of this article shall be used around impaired connections, such as, reducing washers or oversized, concentric, or eccentric knockouts".
Then followed by this sentence.
"Standard locknuts or bushings shall not be the only means for bonding required by this section" ......
That's a little confusing beings it followed the previous sentence. If I am reading its context correctly the sentence is not exclusive to the sentence about the reducing washers or oversized, concentric, or eccentric knockouts. Correct?
So just to be clear for an example.
A punched 3" ko for a 3" emt compression connector still must be bonded by using an accepted means other than the locknut supplied with the connector. Therein, 250.92 (B) (4) "Other listed devices, such as bonding type lock nuts, bushings, or bushings with bonding jumpers". That would include a bonding wedge.
Correct?
250.92 (B)
Correct?