Shujinko
I have a project in an existing building where a 14,000 square foot portion of the building is being renovated for a new tenant. The building has an existing main switchboard; 480Y/277V with a 4000A MCB with GFP protection. The existing building generator is 1500KW/1875KVA, 480Y/277V, Diesel Fuel. All the associated existing ATS's are 4-pole because of the GFP protection on the main switchboard.
The building owner is requiring the new tenant to provide their own separate generator, since the owner is reserving generator capacity for a different future tenant that needs alot of EM power. Since the new tenant for my project will only have a few small plug loads that need to be on generator (optional branch) we are specifying a 20KW/25KVA, 208Y/120V generator and a new ATS connected on the normal side to an existing building 208Y/120V distribution panel . My question is, does the ATS for the new tenant's 20KW generator need to be 3-pole or 4-pole? The way I see it I am considering the following 2 items:
1. The existing building switchboard has a 4000A MCB with GFP at 480Y/277V. And although we are connecting the ATS's normal side to a 208Y/120V existing distribution panel fed from distribution transformer (separately derived system). There still might be possibilities of nuisance trips on the 4000A MCB GFP at the Main Switchboard.
2. If another tenant comes and adds a generator/ATS to the 208Y/120V distribution panel we are connecting to, and both tenants have 3-pole ATS's, I believe we have more of a possibility of nuisance trips of breakers and electrical quality problems.
I am definitely leaning towards a 4-pole ATS but wanted to hear other people's opinion about my concerns and if they're warranted? Appreciate everyone's input in advance.