Installation consists of 4-3 phase circuits feeding motors. 12 ccc installed in one conduit. #12’s on 20 A breakers . They end up on motor starters with overload protection. FLC’ s on each motor is approximately 6A apiece. According to Table 310.15(B)(3)(a), 12 ccc would have to be derated 50% , which wouldn’t correspond with a 20A breaker. Could the overload protection device for these motors be assumed that they would instead meet this requirement, since it would be set below the 15A derated value of conductors? Thanks for any help.