Slide rule. You line up the hp and other inputs. Haven't seen one in a long long time!
Look at 240.4 (D) (7)
#10 ampacity 30 amps.
Also look at 240.4 (G) & Table 240.4 (G) for overload protection.
No, not on a 50 amp breaker.
Well actually for figuring the branch circuit wire size you do not use the motor nameplate amps. You have to use the HP rating as found in Table 430.248. The nameplate on the motor says 5hp at 230V.
Using Table 430.248 says 5hp at 230V use 28 amps. 28 X 1.25% = 35 amps. #8cu wire.
Size of breaker at the panel, use a 40 or 50 amp breaker. Use the Leviton 6-50R receptacle. Pretty much what the electrician before you did.
Not questioning you on 240.4 (d) 7, but why does the square do slip stick give me a 60a fal22060 on #10 wire? Are they utilizing 430.52? So after #10 conductor size 240.4 d 7 doesn’t apply? I Just noticed that the slip stick is from 2008 and is probably somewhat out of date...
See that’s what I came up with as well... and thought I’d be okay....! jamesco pointed out 240.4 d(7)28A * 1.25 = 35A: #10Awg @75C has an ampacity of 35A.
28A * 2.50 = 70A: The circuit breaker could be as large as 70A.
that’s what I also came up with.... and using exception 2 if the breaker isn’t sufficient for starting current I can use exception (c) and actually go up to 300%.... does it mater if it’s not a fal22060 and it’s just a 2 pole miniature square d qo breaker ?28A * 1.25 = 35A: #10Awg @75C has an ampacity of 35A.
Yes you are but that doesn't change the fact that you could go up to 70.Aren't you supposed to try a smaller breaker 1st and as a last resort, this is as large as allowed?
Yeah that makes sense to me, but I can fuse #10s on a 60amp breaker if starting current trips the breaker according to the exceptionAren't you supposed to try a smaller breaker 1st and as a last resort, this is as large as allowed?
Maybe I replied to the wrong person, but after I found out that the plugs are only rated for. 3 hp motor I decided I was going to set a disconnect instead... see that’s why I originally thought it made more sense to install the #10 conductors on 30amp receptacle fused on a 50amp breaker, because later I didn’t want someone to plug in an 50a device that would pull more than the conductors are rated for. So basicslly if I was using a receptacle and plug 240.4 d7 allies and I’m only good for 30amps on #10, but because I’m setting a disconnect with adequate voltage, amperage, and hp rating I can get away with using the exceptions in 430.52, if I needed.... sorry for the mix up/
Because of the 6-50R receptacle installed on the #10 branch circuit wiring that's connected to a 60 amp breaker. It's not idiot proof. What if? What happens when you leave the job and never look back? Get rid of the 50 amp receptacle then ask me your question again.
So a normal square d qo two pole breaker Can be upsized ?240.4(D)(7) doesn't apply.
The circuit breaker doesn't have to specifically be an FAL type.
I completely Agree with you that’s why I thought i thought it made sense of to initially install the 30a receptacle instead of a 50amp. I agree most likely the air compressor will move and they will try and plug something with a 50 amp end into the receptacle and the #10 conductors are not sized for a load over 35 amps.... basically if the receptacle and plug were 5hp rated then I could use this as a type of disconnect snd I see why in a plug receptacle situation why a 50amp receptacle should be fed with #8 and put on a 50amp breaker... now if you were t use a non fused disconnect I should be able to get away with #10’s and a max 70 amp breaker. Not saying that this is what I will do? But if this were a code related question on a test and they eanted to know the minimum size conductor or maximum size breaker 430.52 exception no 2 (c) allows the upsizing for starting current....Because of the 6-50R receptacle installed on the #10 branch circuit wiring that's connected to a 60 amp breaker. It's not idiot proof. What if? What happens when you leave the job and never look back? Get rid of the 50 amp receptacle then ask me your question again.
Unplug the air compressor from the 50 amp receptacle. Move the compressor to another area or room. Does your installation still meet code?