ptonsparky
Tom
- EC - retired
Small pump motor, 15 HP operating on 240v, corner ground delta. Four wire to PP. Grounded conductor bonded to EG in POCO meter socket. EG bonded & Earthed via 1 rod at PP. Fifty (?) year old motor runs so smooth, you would never know there was a problem by listening to it. Long story why I was even there.
Usually rotating the leads helps. Not so this time. Current stayed the same which points to POCO or lateral. Lateral was fine and POCO with bucket truck found nothing at transformers after I left. They did not like the current readings they took after I left and are changing xfmr bank to a Delta with hi leg this morning.
Is this voltage:current imbalance typical? Is it predictive?
| Customer: | ||||||||
| Date: | ||||||||
| % VOLTAGE IMBALANCE | ||||||||
| PHASE | VOLT | Amp | ||||||
| A-B | 252.00 | 41.00 | 4.67 | 0.33 | ||||
| B-C | 248.00 | 47.00 | 0.67 | 6.33 | ||||
| A-C | 242.00 | MAX | MAX-AVG | 34.00 | MAX | MAX-AVG | 5.33 | 6.67 |
| AVG | 247.33 | 252 | 4.67 | 40.67 | 47 | 6.33 | 5.33 | 6.67 |
| STAND DEVIATION | 4.11 | 5.31 | ||||||
| TOTAL IMBALANCE | 2.16% | Investigate | 16.39% | Investigate |